OPC-UA issues with ControlLogix

Our manual does need to be updated to include the connection path addition.

The path depends on the modules the connection is being routed through and the manual for the modules should be referenced.
But in general:

It must be an even number of values separated by commas.

In Ignition, the first connection point is a ControlLogix Ethernet module such as ENET, ENBT
or EN2T module.

ENET, ENBT and EN2T:
1 = Backplane
2 = Ethernet Port

CNB:
1 = Backplane
2 = ControlNet Port

DHRIO:
1 = Backplane
2 = DH+ Channel A
3 = DH+ Channel B

Example:
To connect to the processor in slot 0, the path is 1,4,2,12,1,0


Where:
1 = Backplane
4 = Slot 4, CNB module
2 = ControlNet Port
12 = CN 12
1 = Backplane
0 = Slot 0 - Processor