 Can't connect to the Lookout OPC Server 
Author Message
Cadet
Cadet

Joined: Thu Jul 15, 2010 10:35 pm
Posts: 2
Post Re: Can't connect to the Lookout OPC Server
In server explorer, see the "properties" of LookoutOPCServer. Under registry tab, is the CatIDs set or not?
If it's not registered, run these two commands in "Run",
1. regsvr32 "c:\program files\national instruments\shared\logos\lkopc.dll"
2. "c:\program files\national instruments\shared\logos\lkopc.exe" /regserver"
the directory for Logos may be different.
Have a try.


Thu Jul 15, 2010 10:44 pm
Profile
Captain
Captain

Joined: Thu May 12, 2011 1:00 pm
Posts: 76
Location: Northern California
Post Re: Can't connect to the Lookout OPC Server
This is the only topic I've found relating to the Lookout OPC server (on this forum). I've tried everything to get a connection from my Ignition Server to my Lookout OPC server. It seems no matter what I do I can't even connect to the OPC server via the NI Server Explorer on my Ignition System.
It gives me the error:
"Error Connecting Network Registry: Unable to connect to \\???! Make sure that this computer is on the network, has remote administration enabled, and that both computers are running the remote registry service."
I've tried enabling the permissions for DCOM, OPCEnum and opened ports/programs through the firewalls. I've done everything I can find online about this type of connection... Can't seem to get a connection.

In response to the above post, Yes the CatIDs are set. I've even gone as far as checking the registry permissions.
Does anyone have anything else they can mention that I may try.

This is the error I'm getting from Ignition just in case this helps:
Code:
com.inductiveautomation.ignition.common.opcua.UAException: Could not open secure channel to opc.tcp://192.168.0.230:135/.
com.inductiveautomation.xopc.client.stack.TCPClientChannel.open(TCPClientChannel.java:269)
com.inductiveautomation.xopc.client.stack.TCPClientChannel.getEndpoints(TCPClientChannel.java:81)
com.inductiveautomation.xopc.client.stack.TCPClientChannel.getEndpoints(TCPClientChannel.java:69)
com.inductiveautomation.xopc.client.sropc.ConnectionUtil.getEndpoint(ConnectionUtil.java:65)
com.inductiveautomation.xopc.client.sropc.ConnectionManager.connect(ConnectionManager.java:92)
com.inductiveautomation.xopc.client.sropc.UAServer.setUp(UAServer.java:117)
com.inductiveautomation.xopc.client.sropc.UAServer.access$200(UAServer.java:49)
com.inductiveautomation.xopc.client.sropc.UAServer$3.run(UAServer.java:205)
com.inductiveautomation.ignition.common.execution.impl.BasicExecutionEngine$ThrowableCatchingRunnable.run(BasicExecutionEngine.java:526)
java.util.concurrent.Executors$RunnableAdapter.call(Unknown Source)
java.util.concurrent.FutureTask$Sync.innerRun(Unknown Source)
java.util.concurrent.FutureTask.run(Unknown Source)
java.util.concurrent.ScheduledThreadPoolExecutor$ScheduledFutureTask.access$301(Unknown Source)
java.util.concurrent.ScheduledThreadPoolExecutor$ScheduledFutureTask.run(Unknown Source)
java.util.concurrent.ThreadPoolExecutor$Worker.runTask(Unknown Source)
java.util.concurrent.ThreadPoolExecutor$Worker.run(Unknown Source)
java.lang.Thread.run(Unknown Source)


I'll also post this on the NI Forum. Thanks.


Wed Dec 14, 2011 1:59 pm
Profile
Captain
Captain

Joined: Thu May 12, 2011 1:00 pm
Posts: 76
Location: Northern California
Post Re: Can't connect to the Lookout OPC Server
I'll also add that the Ignition System is running on Windows 7 and the Lookout OPC server is on Windows XP.


Wed Dec 14, 2011 2:06 pm
Profile
Moderator
Moderator

Joined: Mon Oct 27, 2008 4:10 pm
Posts: 1980
Location: Folsom, CA
Post Re: Can't connect to the Lookout OPC Server  Topic is solved
techerdone, you're trying to connect to what appears to be an OPC-DA server with an OPC-UA connection. You'll need to install the COM module and create a DA connection instead.

_________________
Kevin Herron
Software Developer
Inductive Automation


Wed Dec 14, 2011 2:17 pm
Profile WWW
Captain
Captain

Joined: Thu May 12, 2011 1:00 pm
Posts: 76
Location: Northern California
Post Re: Can't connect to the Lookout OPC Server
Thanks, Kevin. Nailed it.


Mon Apr 23, 2012 11:17 am
Profile
Display posts from previous:  Sort by  
Post new topic This topic is locked, you cannot edit posts or make further replies.  [ 5 posts ] 


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to: