Post Connect Win911 to Ignition
Can I connect Win911 to Ignition using the OpcCom Module?

Is there any other way to connect Win911 to Ignition so that an Ack get through to Ignition?

_________________
Erik Burns, PE


Tue May 10, 2011 10:06 am
Profile WWW
General
General

Joined: Fri Jan 02, 2009 4:53 am
Posts: 172
Location: Jacksonville, NC
Post Re: Connect Win911 to Ignition
Erik,

I have used SCADAPhone (very similar to Win911) on a couple of jobs with Ignition. What I normally do for the Ack back to Ignition is set up a dummy register in the PLC, and have SCADAPhone/Ignition look at that register for the "Global Acknowledge." Not the most ideal setup, but it does work.

Thanks.
Joe


Tue May 10, 2011 10:29 am
Profile
General
General

Joined: Wed Feb 24, 2010 5:56 pm
Posts: 616
Post Re: Connect Win911 to Ignition
you can use a odbc to opc server. kepware makes one.

http://www.kepware.com/Spec_Sheets/ODBC ... Driver.asp


Tue May 10, 2011 4:15 pm
Profile
Cadet
Cadet

Joined: Fri Feb 04, 2011 10:34 am
Posts: 8
Location: Lake Mathews, CA
Post Re: Connect Win911 to Ignition
You can't directly connect to Win911 using the OPC-COM module. I had to use KepWare, then connect Win911 to Kepware and Ignition to Kepware using the OPC-COM module, you can use OPC-UA to connect to Kepware, but its a few more steps because you have to set up certificates. Also note that the there is a bug with OPC-UA connection dropping out and not reconnecting. I don't know if this has been resolved yet.

Richard


Tue May 24, 2011 9:51 pm
Profile
Cadet
Cadet

Joined: Fri Feb 04, 2011 10:34 am
Posts: 8
Location: Lake Mathews, CA
Post Re: Connect Win911 to Ignition
Set Win911 alarm to acknowledge on return to normal, then you are going to have to write some script that sets a tag when in alarm condition and resets it when an acknowledge button is pressed in Ignition.


Wed Jun 22, 2011 10:06 pm
Profile
Trooper
Trooper

Joined: Thu Jan 05, 2012 12:26 pm
Posts: 14
Post Re: Connect Win911 to Ignition
TopView SQL from Exele can do what you need by using the SQL tables in Ignition.
http://www.exele.com/Products/TopView/topview_about.htm

We have added some details of integrating TopView SQL to Ignition.
http://www.exele.com/Products/TopView/s ... /index.htm


Fri Feb 24, 2012 6:04 pm
Profile
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to: