Sparkline Chart with indirect tag history errors
|
||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
|
|
Page 1 of 1 |
[ 9 posts ] |
| Print view | Previous topic | Next topic |
| Author | Message |
|---|---|
|
General ![]() Joined: Mon Apr 04, 2011 4:40 pm Posts: 368 Location: Hatfield, PA |
Hey guys,
I upgraded my servers to 7.5.1 over the weekend and now on pages that have sparkline charts with indirect tag history I get this error everytime it refreshed the tag history data, the sparkline goes red and then it actually updated the data and looks fine until the next time it refreshes. Quote: Message: Error running query:<br>TagHistory(paths=[kill floor main plc/synchronization/line -1/current difference], start=Mon Jul 23 15:07:08 EDT 2012, end=Mon Jul 23 15:22:08 EDT 2012, flags=0)@15000ms<br>On: Line Sync.Line Sync.Sparkline Chart.data Time: Mon Jul 23 3:22:08PM Severity: WARN Logger: ignition.application.binding.TagHistoryAdapter Stack Trace: java.lang.Exception: Error running query:<br>TagHistory(paths=[kill floor main plc/synchronization/line -1/current difference], start=Mon Jul 23 15:07:08 EDT 2012, end=Mon Jul 23 15:22:08 EDT 2012, flags=0)@15000ms<br>On: Line Sync.Line Sync.Sparkline Chart.data <br> at com.inductiveautomation.factorypmi.application.gateway.QueryManager\$QueryExecutor.run(QueryManager.java:317) <br> at java.lang.Thread.run(Unknown Source) <br>Caused by: com.inductiveautomation.ignition.client.gateway_interface.GatewayException: null <br> at com.inductiveautomation.ignition.client.gateway_interface.GatewayInterface.newGatewayException(GatewayInterface.java:312) <br> at com.inductiveautomation.ignition.client.gateway_interface.GatewayInterface.sendMessage(GatewayInterface.java:286) <br> at com.inductiveautomation.ignition.client.gateway_interface.GatewayInterface.sendMessage(GatewayInterface.java:243) <br> at com.inductiveautomation.ignition.client.gateway_interface.GatewayInterface.runTagHistoryQuery(GatewayInterface.java:626) <br> at com.inductiveautomation.factorypmi.application.gateway.GWITagHistoryProvider.query(GWITagHistoryProvider.java:16) <br> at com.inductiveautomation.ignition.common.sqltags.history.cache.TagHistoryCache.query(TagHistoryCache.java:193) <br> at com.inductiveautomation.factorypmi.application.gateway.TagHistoryQuery.execute(TagHistoryQuery.java:34) <br> at com.inductiveautomation.factorypmi.application.gateway.QueryManager\$Query.execute(QueryManager.java:701) <br> at com.inductiveautomation.factorypmi.application.gateway.QueryManager\$Query.access\$500(QueryManager.java:674) <br> at com.inductiveautomation.factorypmi.application.gateway.QueryManager\$QueryExecutor.run(QueryManager.java:315) <br> ... 1 more <br>Caused by: java.lang.NullPointerException <br> at com.inductiveautomation.ignition.gateway.sqltags.history.query.loaders.DatasourceHistoryLoader.getEffectiveWindowSizeMS(DatasourceHistoryLoader.java:178) <br> at com.inductiveautomation.ignition.gateway.sqltags.history.query.HistoryWriter.calculateBlockSize(HistoryWriter.java:203) <br> at com.inductiveautomation.ignition.gateway.sqltags.history.query.HistoryWriter.execute(HistoryWriter.java:236) <br> at com.inductiveautomation.ignition.gateway.sqltags.SQLTagsManagerImpl.queryHistory(SQLTagsManagerImpl.java:826) <br> at com.inductiveautomation.ignition.gateway.servlets.gateway.functions.QueryTagHistory.invoke(QueryTagHistory.java:105) <br> at com.inductiveautomation.ignition.gateway.servlets.Gateway.doPost(Gateway.java:398) <br> at javax.servlet.http.HttpServlet.service(HttpServlet.java:637) <br> at javax.servlet.http.HttpServlet.service(HttpServlet.java:717) <br> at com.inductiveautomation.ignition.gateway.bootstrap.MapServlet.service(MapServlet.java:85) <br> at org.apache.catalina.core.ApplicationFilterChain.internalDoFilter(ApplicationFilterChain.java:290) <br> at org.apache.catalina.core.ApplicationFilterChain.doFilter(ApplicationFilterChain.java:206) <br> at org.apache.catalina.core.StandardWrapperValve.invoke(StandardWrapperValve.java:233) <br> at org.apache.catalina.core.StandardContextValve.invoke(StandardContextValve.java:191) <br> at org.apache.catalina.core.StandardHostValve.invoke(StandardHostValve.java:128) <br> at org.apache.catalina.valves.ErrorReportValve.invoke(ErrorReportValve.java:102) <br> at org.apache.catalina.core.StandardEngineValve.invoke(StandardEngineValve.java:109) <br> at org.apache.catalina.connector.CoyoteAdapter.service(CoyoteAdapter.java:286) <br> at org.apache.coyote.http11.Http11Processor.process(Http11Processor.java:845) <br> at org.apache.coyote.http11.Http11Protocol\$Http11ConnectionHandler.process(Http11Protocol.java:583) <br> at org.apache.tomcat.util.net.JIoEndpoint\$Worker.run(JIoEndpoint.java:447) <br> at java.lang.Thread.run(null) <br> Stack Trace: com.inductiveautomation.factorypmi.application.gateway.QueryManager$QueryExecutor.run(QueryManager.java:317) java.lang.Thread.run(Unknown Source) Also, if it means anything, the sparkline charts are part of templates as well. _________________ There are 10 types of people in this world, those who understand binary and those who don't. Doug Keller Electronics Project Manager Clemens Food Group |
| Mon Jul 23, 2012 11:26 am |
|
|
Moderator ![]() Joined: Sun Apr 02, 2006 3:43 pm Posts: 2171 |
I doubt it has anything to do with the type of chart, but instead perhaps with the binding settings & some sort of issue with the data. In particular, take a look and see if the binding on "data" is set to a sample size of "Natural". If so, when you look at the console in the gateway, do you see any messages like "No scan class information found for tags"?
If it's not "natural", let me know. Otherwise I would recommend trying either on-change or fixed. Ultimately, it's trying to figure out what the tag's scan class was running at, and is failing for some reason. If you want, you can call in and we can try to track down what's really going on, but trying one of the other modes should at least work around it for now. Regards, _________________ Colby Clegg Inductive Automation Software Development |
| Mon Jul 23, 2012 2:36 pm |
|
|
General ![]() Joined: Mon Apr 04, 2011 4:40 pm Posts: 368 Location: Hatfield, PA |
Well, I think the actual problem is this:
Quote: TagHistory(paths=[kill floor main plc/synchronization/line -1/current difference] Even though it's supposed to be getting an actual number for "line -1" it's putting a -1 in there, of course there is no line -1. It does this everytime it refreshes. Instead of using the indirection it's putting -1 in for the indirect value. It was working fine before the upgrade to 7.5.1 (from 7.5.0). _________________ There are 10 types of people in this world, those who understand binary and those who don't. Doug Keller Electronics Project Manager Clemens Food Group |
| Mon Jul 23, 2012 2:42 pm |
|
|
Moderator ![]() Joined: Sun Apr 02, 2006 3:43 pm Posts: 2171 |
Ah, ok, I'll take a look at that scenario. However, my main suggestion still applies: this is an error that should only be able to happen if using "natural" results. If you can use a different result type, you should be able to get around it until we fix the main issue.
Regards, _________________ Colby Clegg Inductive Automation Software Development |
| Mon Jul 23, 2012 2:59 pm |
|
|
General ![]() Joined: Mon Apr 04, 2011 4:40 pm Posts: 368 Location: Hatfield, PA |
Will do, I'll take a look at that tomorrow.
Also, after thinking about it the indirection is pointing to a user defined datatype and the chart is part of a template whose drop target is the user defined data type. Maybe all of that has something to do with it too. FYI. _________________ There are 10 types of people in this world, those who understand binary and those who don't. Doug Keller Electronics Project Manager Clemens Food Group |
| Mon Jul 23, 2012 3:05 pm |
|
|
General ![]() Joined: Mon Apr 04, 2011 4:40 pm Posts: 368 Location: Hatfield, PA |
FYI, Changing the sample size to fixed seems to have gotten rid of that error on the client.
However I'm still getting a ton of these errors in the gateway console: Attachment: TagHistoryError1.png [ 12.18 KiB | Viewed 656 times ] _________________ There are 10 types of people in this world, those who understand binary and those who don't. Doug Keller Electronics Project Manager Clemens Food Group |
| Tue Jul 24, 2012 3:27 am |
|
|
Moderator ![]() Joined: Sun Apr 02, 2006 3:43 pm Posts: 2171 |
Hi,
It seems to be having some difficulty dealing with tags that don't exist (the paths have -1, so I'm guessing these are happening in the designer when you don't have a valid property there). It shouldn't hurt anything, but I'll take a look- it's supposed to just return bad quality. Regards, _________________ Colby Clegg Inductive Automation Software Development |
| Fri Jul 27, 2012 3:44 pm |
|
|
Moderator ![]() Joined: Sun Apr 02, 2006 3:43 pm Posts: 2171 |
Looking at your latest log, I think we've fixed all of the actual errors. The log message about "no tag info found" is a nuisance, but technically correct, and useful for troubleshooting. However, I've changed that logger to only log once per minute, so it should cut down on the number of messages.
Regards, _________________ Colby Clegg Inductive Automation Software Development |
| Mon Aug 13, 2012 9:10 am |
|
|
General ![]() Joined: Mon Apr 04, 2011 4:40 pm Posts: 368 Location: Hatfield, PA |
Ok, that's fair. Thank you!
_________________ There are 10 types of people in this world, those who understand binary and those who don't. Doug Keller Electronics Project Manager Clemens Food Group |
| Mon Aug 13, 2012 11:13 am |
|
|
|