It is currently Sat May 25, 2013 2:10 am
Post new topic Reply to topic  [ 4 posts ]
 Modbus Addressing on Moxa
Author Message
Trooper
Trooper
Post Modbus Addressing on Moxa
I have the addressing for the Moxa device from the manual, but can't get the values to show up in Ignition.
Attached is the screen shot of the manual, with the address I am trying to get.
What do I need to enter in the device configuration?
Thu Aug 09, 2012 1:19 pm
Profile
Moderator
Moderator
Post Re: Modbus Addressing on Moxa
In the address map you will configure these as 32-bit Input Registers starting from modbus address 1.
_________________
Kevin Herron
Software Developer
Inductive Automation
Thu Aug 09, 2012 1:26 pm
Profile WWW
Trooper
Trooper
Thank you that worked.
Any way to get the data to come in as float? Currently a temperature value of 75.3 degrees comes in as 753. I tried changing it from Int32 to Float, but that does not give me a value.
Mon Aug 13, 2012 8:43 am
Profile
Moderator
Moderator
You'll have to apply scaling or an expression to the tag in the designer in that case. Designating it as a float in the modbus configuration assumes that the value is in IEEE floating point format, not just the correct value multiplied by some factor.
_________________
Kevin Herron
Software Developer
Mon Aug 13, 2012 8:49 am
Profile WWW
Display posts from previous:  Sort by
Who is online
Users browsing this forum: No registered users and 6 guests
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum
Search for:
Jump to: