Sorry if it is off topic or too inocent question, but i need to be sure
I need to communicate from my java application to a SLC5/05 plc. Can i use Ignition allen bradley driver modules directly for this, with no OPC-server involved?
regards,
PF
Sorry if it is off topic or too inocent question, but i need to be sure
I need to communicate from my java application to a SLC5/05 plc. Can i use Ignition allen bradley driver modules directly for this, with no OPC-server involved?
regards,
PF
No, the modules are drivers for Ignition’s UA server, not general purpose communication libraries.
Ok, thanks for the reply.